My home charging project is close enough to completion that it's time to share it. This thread is a bit of an installation walk-thru, but I'll start with the finished product.
The EVSE I chose is a Clipper Creek HCS-50, but I've modified it by separating the charging cable from the box.
The 25-foot long, 40 amp charging cord discretely tucks into the outside alcove of the garage. The holster / cable hanger is from OpenEVSE and mounted to a piece of oil-rubbed mahogany to match the garage doors. The EVSE itself is installed inside the garage to keep the installation looking clean.
My original intent was to mount the complete EVSE box in this alcove (hence the patched bolt holes you can see on the stucco), but this last minute inspiration to separate the cable from the box won the day.
Since 2019 I've been happily Level 1 charging my BMW i3 mainly at work, or infrequently at home either L1 or sometimes L2 (Duosida dual voltage 16A EVSE), running an extension cord either to an outside 120 volt receptacle, or through the doors to a 240 volt socket I installed inside on the back wall of the garage. I didn't really "need" 40A capability for that car's relatively tiny battery, and knew the Clipper Creek was going to be an effort to install (as detailed in this thread). So the HCS-50 sat untouched on my workbench for 9 months.
Upon the addition of the ID.4 to our household, the time had come to install the Clipper Creek HCS-50.
We park on the street — my detached garage is more of a workshop than any place to store a vehicle, and we don't have a driveway. So while I had some flexibility with the extension cord I use to charge the i3, the HCS-50's 25 ft. cable constrained my installations options.
With the L2 charging cord extending from the square gray electrical box down low (photo), I've maximized its 25-foot length for the greatest reach out to the street. I also added a 240 volt / 20 amp receptacle (photo: brown weatherproof cover — note it's a split receptacle with 240v up top / 120v on the bottom) to this more convenient location outside of the garage, so I can simultaneously charge my i3, without having to open the garage doors and run the cord to the back wall. I'm really happy with how tidy this turned out.
I generally don't have to worry about our driveway being blocked, so the primary charging position is a given. Both cars have their charge ports on the right side, so I needed to maximize the available 25 feet of the charging cord. Had I stuck with my original plan -- mounting the EVSE box outside in the alcove and high up -- the cord would have been too short by a few feet, and I'd need to purchase a longer cable or an extension. Twenty-five feet with no extensions is the maximum permitted length by electrical code, but more importantly, it would be costly. To protect the cord and prevent a tripping hazard, I lay down this heavy rubber door mat (photo) where it crosses the sidewalk. I'm considering routing open the sidewalk joint to give the cable a deeper place to nest, but this current arrangement seems adequate.
About two months ago, having already purchased the wire and some of the other materials, I kicked off the project. The entire installation wasn't a true two months' effort — some of it was waiting for parts to arrive, or me just getting busy with work-work, plus an unforeseen setback or two. I'll walk through that further down.
I'm not a licensed electrician and am sharing this with the caveat that I've been doing my own electrical for quite a while and am comfortable with the work I did, but also know that I'm not 100% code compliant (I'll point those areas out that I'm aware of). I welcome to any criticism / critique as I, too, am always learning. For instance, in the second photo, I'm supposed to label this box "“For Use With Electric Vehicles" and I need to install a placard indicating where the shut-off switch is located, since it is not in view of the charging cable. The holster should be no greater than 4 feet off the ground, and the gray box should be at least 24" off the ground (my interpretation as the code refers to "outlets" not "receptacles"). For your reference, I'm using a guide from my utility that summarizes NEC and state code (https://www.pge.com/includes/docs/pdfs/about/environment/pge/electricvehicles/ev5pt3.pdf).
Let me mention some of the tools I used opening the concrete which I consider could be "less common" than what might be on the typical workbench.
First and foremost my eager 9 year old helper held the garden hose while I cut concrete, he vacuumed, cleaned out the trench, pulled wire while I pushed it from the other end, and cut and shrank the heat shrink. He's holding a Bosch Bulldog hammer drill for coring the concrete and cutting larger holes in concrete and stucco. He's sitting next to a cheapo Harbor Freight demo hammer which isn't great but gets the job done busting concrete, a pneumatic chipper for breaking up the smaller concrete chunks, and an oversized angle grinder with a 9 inch concrete wheel.
First item of work was what I was dreading most: opening up 6 feet of concrete sidewalk to run conduit from my main panel to the fence. The concrete cutting is messy once water is on the blade, so I put up plastic sheeting. After cutting the opening with a 9-inch angle grinder, I used the demo hammer to bust up the concrete. I got lucky with the rebar and didn't cut it. I also knew I had drain pipe and an existing electrical conduit down there, so proceeded carefully around them both.
Electrical conduit should be set at minimum 6" below a concrete slab, but with drain line in the way here and a lateral electrical conduit crossing on the other end of the trench, this is as deep as I'm willing to set it. I'll nest it with sand and compactable gravel, so if I ever need to open the concrete again, the conduit won't be embedded. The run straight across from the electrical panel to the other side will be obvious, so I'm not worried about somebody aka my future self "accidentally" finding it.
For the drop in, I used a box elbow off the panel to a pre-bent aluminum elbow, then a liquid-tight transition to PVC for the under-slab. My intent with the liquid tight (which is flexible) was to decouple the house-mounted conduit from the sidewalk-mounted conduit, to minimize the chance of cracking or pulling apart, since the two surfaces move independently. I probably need more of an 'S' bend in the LT conduit for this to work as intended, but I'll know in a few years if my plan worked, or needs to be revisited.
The metallic liquid tight conduit is galvanized steel inside with a thermoplastic jacket. It isn't extremely flexible — this here is about its tightest bend for the 1-inch size. It's easy to cut with a recip saw, and the end fittings simply screw on internally.
The EVSE I chose is a Clipper Creek HCS-50, but I've modified it by separating the charging cable from the box.
The 25-foot long, 40 amp charging cord discretely tucks into the outside alcove of the garage. The holster / cable hanger is from OpenEVSE and mounted to a piece of oil-rubbed mahogany to match the garage doors. The EVSE itself is installed inside the garage to keep the installation looking clean.
My original intent was to mount the complete EVSE box in this alcove (hence the patched bolt holes you can see on the stucco), but this last minute inspiration to separate the cable from the box won the day.
Since 2019 I've been happily Level 1 charging my BMW i3 mainly at work, or infrequently at home either L1 or sometimes L2 (Duosida dual voltage 16A EVSE), running an extension cord either to an outside 120 volt receptacle, or through the doors to a 240 volt socket I installed inside on the back wall of the garage. I didn't really "need" 40A capability for that car's relatively tiny battery, and knew the Clipper Creek was going to be an effort to install (as detailed in this thread). So the HCS-50 sat untouched on my workbench for 9 months.
Upon the addition of the ID.4 to our household, the time had come to install the Clipper Creek HCS-50.
We park on the street — my detached garage is more of a workshop than any place to store a vehicle, and we don't have a driveway. So while I had some flexibility with the extension cord I use to charge the i3, the HCS-50's 25 ft. cable constrained my installations options.
With the L2 charging cord extending from the square gray electrical box down low (photo), I've maximized its 25-foot length for the greatest reach out to the street. I also added a 240 volt / 20 amp receptacle (photo: brown weatherproof cover — note it's a split receptacle with 240v up top / 120v on the bottom) to this more convenient location outside of the garage, so I can simultaneously charge my i3, without having to open the garage doors and run the cord to the back wall. I'm really happy with how tidy this turned out.
I generally don't have to worry about our driveway being blocked, so the primary charging position is a given. Both cars have their charge ports on the right side, so I needed to maximize the available 25 feet of the charging cord. Had I stuck with my original plan -- mounting the EVSE box outside in the alcove and high up -- the cord would have been too short by a few feet, and I'd need to purchase a longer cable or an extension. Twenty-five feet with no extensions is the maximum permitted length by electrical code, but more importantly, it would be costly. To protect the cord and prevent a tripping hazard, I lay down this heavy rubber door mat (photo) where it crosses the sidewalk. I'm considering routing open the sidewalk joint to give the cable a deeper place to nest, but this current arrangement seems adequate.
About two months ago, having already purchased the wire and some of the other materials, I kicked off the project. The entire installation wasn't a true two months' effort — some of it was waiting for parts to arrive, or me just getting busy with work-work, plus an unforeseen setback or two. I'll walk through that further down.
I'm not a licensed electrician and am sharing this with the caveat that I've been doing my own electrical for quite a while and am comfortable with the work I did, but also know that I'm not 100% code compliant (I'll point those areas out that I'm aware of). I welcome to any criticism / critique as I, too, am always learning. For instance, in the second photo, I'm supposed to label this box "“For Use With Electric Vehicles" and I need to install a placard indicating where the shut-off switch is located, since it is not in view of the charging cable. The holster should be no greater than 4 feet off the ground, and the gray box should be at least 24" off the ground (my interpretation as the code refers to "outlets" not "receptacles"). For your reference, I'm using a guide from my utility that summarizes NEC and state code (https://www.pge.com/includes/docs/pdfs/about/environment/pge/electricvehicles/ev5pt3.pdf).
Let me mention some of the tools I used opening the concrete which I consider could be "less common" than what might be on the typical workbench.
First and foremost my eager 9 year old helper held the garden hose while I cut concrete, he vacuumed, cleaned out the trench, pulled wire while I pushed it from the other end, and cut and shrank the heat shrink. He's holding a Bosch Bulldog hammer drill for coring the concrete and cutting larger holes in concrete and stucco. He's sitting next to a cheapo Harbor Freight demo hammer which isn't great but gets the job done busting concrete, a pneumatic chipper for breaking up the smaller concrete chunks, and an oversized angle grinder with a 9 inch concrete wheel.
First item of work was what I was dreading most: opening up 6 feet of concrete sidewalk to run conduit from my main panel to the fence. The concrete cutting is messy once water is on the blade, so I put up plastic sheeting. After cutting the opening with a 9-inch angle grinder, I used the demo hammer to bust up the concrete. I got lucky with the rebar and didn't cut it. I also knew I had drain pipe and an existing electrical conduit down there, so proceeded carefully around them both.
Electrical conduit should be set at minimum 6" below a concrete slab, but with drain line in the way here and a lateral electrical conduit crossing on the other end of the trench, this is as deep as I'm willing to set it. I'll nest it with sand and compactable gravel, so if I ever need to open the concrete again, the conduit won't be embedded. The run straight across from the electrical panel to the other side will be obvious, so I'm not worried about somebody aka my future self "accidentally" finding it.
For the drop in, I used a box elbow off the panel to a pre-bent aluminum elbow, then a liquid-tight transition to PVC for the under-slab. My intent with the liquid tight (which is flexible) was to decouple the house-mounted conduit from the sidewalk-mounted conduit, to minimize the chance of cracking or pulling apart, since the two surfaces move independently. I probably need more of an 'S' bend in the LT conduit for this to work as intended, but I'll know in a few years if my plan worked, or needs to be revisited.
The metallic liquid tight conduit is galvanized steel inside with a thermoplastic jacket. It isn't extremely flexible — this here is about its tightest bend for the 1-inch size. It's easy to cut with a recip saw, and the end fittings simply screw on internally.